    Hi: on a TT system what Ze would you use to base a circuit design on.

    Where it says on the EIC Electrode resistance is that a standard test for Ze or is it the actual resistance of the rod.



    If putting 2 ring mains through the same hole in Joists there are 4 cables and 2 circuits do you rate it as 2 circuits for Cfs

    finally if half your circuit lenth is pulled through joists and half in plaster ie downstairs sockets is it C or what do you reakon

    Cheers
    W J
     
  2. Sponsored Links
  3. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    36,790
    Thanks Received:
    1,262
    Country:
    United Kingdom
    The maximum laid down in the OSG?

    I would measure Ze after rod installation.

    2 circuits.

    A C?

    You mean installation method?

    I would say that was Method 1.
     
  4. comms

    comms

    Joined:
    13 Nov 2004
    Messages:
    882
    Thanks Received:
    8
    Location:
    Berkshire
    Country:
    United Kingdom
    Take a reading for Ze.
    Use efli meter and test Ze this can be used as electrode resistance (Ra).
    Same circuit but count as 4 cables.
    C ?
     
  5. comms

    comms

    Joined:
    13 Nov 2004
    Messages:
    882
    Thanks Received:
    8
    Location:
    Berkshire
    Country:
    United Kingdom
    Beat me to it securespark.
     
  6. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    36,790
    Thanks Received:
    1,262
    Country:
    United Kingdom
    What are these strange letters of which you speak?

    I'm not familiar with them... :oops:

    Send secure back to the classroom...
     
  7. comms

    comms

    Joined:
    13 Nov 2004
    Messages:
    882
    Thanks Received:
    8
    Location:
    Berkshire
    Country:
    United Kingdom
    If your on about the C ...I havent got a clue, I thought the same as you he was after installation method & yep I'd go with 1.
     
  8. oldspark

    oldspark

    Joined:
    22 Dec 2004
    Messages:
    87
    Thanks Received:
    1
    Country:
    United Kingdom
    Sorry..... C is on the cert for PVC cables in non metallic trunking
    OS
     
  9. davy_owen_88

    davy_owen_88

    Joined:
    17 Nov 2006
    Messages:
    1,680
    Thanks Received:
    2
    Location:
    West Glamorgan
    Country:
    United Kingdom
    Could you clarify what the options are. On the forms I have it would be A as there is no conduit involved but C on these forms stands for PVC cables in non-metallic conduit (not trunking...). Is that what you meant?

    Davy
     
  10. Sponsored Links
  11. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,993
    Thanks Received:
    1,354
    Location:
    Leeds
    Country:
    United Kingdom
  12. oldspark

    oldspark

    Joined:
    22 Dec 2004
    Messages:
    87
    Thanks Received:
    1
    Country:
    United Kingdom
    Sorry for confusing you all. got most of the answers apart from the installation one, as I said if half the lenth of your circuit is pulled through joists and half is drawn into pvc conduit and then plastered what is the correct installation method to record on the cert.
    know what I'm after now??

    Os
     
  13. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,993
    Thanks Received:
    1,354
    Location:
    Leeds
    Country:
    United Kingdom
    Go for the worst case scenario, so it would be listed as wiring type 'C'
     
  14. davy_owen_88

    davy_owen_88

    Joined:
    17 Nov 2006
    Messages:
    1,680
    Thanks Received:
    2
    Location:
    West Glamorgan
    Country:
    United Kingdom
    You didn't mention the conduit before :p In that case put it as C for the same reason as RF.
     
  15. oldspark

    oldspark

    Joined:
    22 Dec 2004
    Messages:
    87
    Thanks Received:
    1
    Country:
    United Kingdom
    Cheers: sometimes you need to clarify.

    Os :)
     
  16. ricicle

    ricicle

    Joined:
    14 Sep 2006
    Messages:
    6,343
    Thanks Received:
    382
    Location:
    Gloucestershire
    Country:
    United Kingdom
    Where the bloody hell did those codes come from? :confused:
     
  17. davy_owen_88

    davy_owen_88

    Joined:
    17 Nov 2006
    Messages:
    1,680
    Thanks Received:
    2
    Location:
    West Glamorgan
    Country:
    United Kingdom
    They are on the NIC electrical installation cert.
     