In a way, logic does seem to make the regs. confusing.Exactly. 701.415.2(vi) appears to be saying that if all the e-p-cs are already adequately connected together (electrically), they don't need to be additionally connected together locally (by 'supplementary bonding') - which seems to me to be little more than a statement of the obvious, for any location.Yes. Does that not mean that supplementary bonding is not necessary when the e-c-ps are already bonded - i.e. by bonding elsewhere.
No - and that's my point. 701.415.2 says that supplementary bonding can anly be omitted only if all three of 701.415.2(iv), 701.415.2(v) and 701.415.2(vi) are satisfied. In other words, if there is no RCD protection (i.e.701.415.2(v) not satisfied), then you have to have supplementary bonding even if all the e-p-cs present are already adequately connected together (electrically). That is what I was suggesting appears very illogical - do you agree?This surely means that without RCDs bonding may be needed - if above conditions are not met - but with an RCD it may be omitted - even if above conditions are not met.
It presumably means that even WITH an RCD if (iv) and (vi) are not met we still have to apply supplementary bonding.