can anyone help i turn boiler on it makes clicking noise runs for about 5 mins then the red cut out button comes on is it airlocked do u know where bleed valve is thanks
Would it run for five minutes if there was a air lock?
If everything is OK except the 5 minute limit, Then I would suspect the solinoid. The reason being: it comprises a coil of wire which makes a electro magnet. Coils go faulty when the wire breaks and the break opens up due to heat. So it may well operate while cool but only until it gets heated up.
What happens if you try to re light it? (a) straight after lock out and (b) after it's had time to cool off.