• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Still no Hot Water

Joined
21 Sep 2009
Messages
101
Reaction score
3
Country
United Kingdom
Just changed the Diverter Valve in a Vaillant Turbomax 824e and I am still getting an issue with the DHW.

The Boiler fires up up when I demand Hot Water but it never gets hot, infact not even luke warm before the Boiler goes off but will then fire up again, get luke warm and shut off again and this continues everytime.

Do you think there is an issue with the Aqua Sensor or does anyone have any other suggestions?
 
Blocked plate he.
Did you not check this before replacing the div valve?
What made you think the div vlv was kippered?
 
No did not check it as had heating but no HW and in past experiences replacing the DV has always fixed this problem for me.
 
No did not check it as had heating but no HW and in past experiences replacing the DV has always fixed this problem for me.

Sorry for the late reply, you were correct Heat Exchanger it was but the DV was kippered too lol.

Many thanks.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top