Strange Large Single Phase motor??

Joined
27 Sep 2004
Messages
1,300
Reaction score
83
Country
United Kingdom
Hi all. I have a large motor which I need to connect up. Its for grinding wheat on a mill. The rating plate says 240V single phase. 25A FLC. 1440 RPM However inside the terminal box there are the following connections. Z1 & Z2. A1, A2, A3, A4 and 1 & 3. This motor was before I saw it connected to a handle type of starter, similar to the old star / delta starters. Can someone point me in the right direction as to how to connect it, and on a new starter suitable for it. Not come across one like this before!!

Thanks very much. Chris
 
Sponsored Links
Sounds like a capacitor start and/or run or possible split phase motor. The Z connections are normally the start winding.

A1 A2 possibly main winding. 1 and 3 could be a capacitor. A3 and A4 maybe another speed or second capacitor.

Thats as much as I remember off the top of my head but it's a start.
 
Sponsored Links
Yes was just reading that thread! I guess my motor is also a Brook Crompton although its not here to see that. Now to find a compatable starter..
 
Interesting,I have seen several motors on small feed mills in the past rated 480/960 volt,with a hand cranked series parallel starter.These were all installed in rural areas where only a 3 wire single phase supply was available.Your motor sounds like a lower voltage version these,has it got a centrifugal switch on the end of it ?.
 
Also, the chap thought that the overload required would be half of the FLC as the windings are paralleled up?
 
I still think you will need a capacitor in series with the start winding,Please do not be tempted to put it DOL in parallel or you will most likely take out your service fuse.
 
I still think you will need a capacitor in series with the start winding,Please do not be tempted to put it DOL in parallel or you will most likely take out your service fuse.
Some motors are constructed with the start winding mechanically out of phase with the run winding and do not need a capacitor. In fact a capacitor may even negate the mechanical phase shift and delay or prevent the motor reaching normal speed.

Use the data sheet and/or technical assist from the manufacturers to be 100% certain of getting it (almost) right.
 
hi there,
i dont know if you have sorted your problem but i just stumbled across this topic and i may be able to help!
i specialise in electric motor repair and don't have a problem in sharing info!
what you have is a series/parallell motor that needs a special starter and also start and run capacitors for it to work.
let me know if you require any further info.

regards

andy
 