T&E conduit recommendation

Joined
8 Apr 2008
Messages
7
Reaction score
0
Location
London
Country
United Kingdom
I've got to chase a path for two 6mm T&E and two 2.5 T&E in a kitchen floor.

Wondering if you pros could give me recommendation for best way to do this?

Would one 25mm PVC conduit for two 6mm T&E (Electric cooker & oven) be acceptable and one 25mm conduit for two 2.5mm T&E

Could I use oval conduit or round one?

The PVC conduit has to go around a bend. Do I need to buy standard bend for this or could I bend the PVC myself?

Any help be appreciated. ;)
 
Sponsored Links
25mm seems a bit small. Not only will you struggle to pull 2no. 6.0mm² through a single tube, but there will also be things like grouping factors to consider on what will be potentially quite well loaded cables.

Could you not put a 3" duct in or something like that?

I also don't like to see PVC t&e cables buried in a floor.
 
Thanks for quick reply.

"I also don't like to see PVC t&e cables buried in a floor."

What would you use instead?

As for using 3" duct you reckon this is the way to go ?
 