Tado wireless smart thermostat wiring to Baxi Neta Tec 33 GA

Joined
1 Nov 2026
Messages
5
Reaction score
3
Country
United Kingdom
Hi All,

Bought the Tado wireless thermostat kit with receiver. Followed instructions but unfortunately can’t get the receiver to communicate with the boiler properly.

Using the low voltage on the M2 connection block doesn’t seem to communicate. Do I need to disconnect the old Danfos room thermostats from the boiler?

Added a couple of pictures that’s hopefully can help.

Many thanks.
 

Attachments

  • IMG_6502.jpeg
    IMG_6502.jpeg
    625.8 KB · Views: 24
  • IMG_6503.jpeg
    IMG_6503.jpeg
    437.8 KB · Views: 24
  • IMG_6513.jpeg
    IMG_6513.jpeg
    314.5 KB · Views: 25
The house has 1 Thermostat up stairs and one down stairs
Yep zonal heating. You have broken the circuit for both by replacing 1 thermostat.
To get this to work, either:

wire in a Tado for each zone, wire back in the Danfoss’ and then have the Tado as a switch live, but you’d still need to operate each zone with existing thermostats, or

remove the actuators for each zone, manually open the spindles and have a single up and down zone.
 
I’d prefer to have tado for each zone, how would I go about doing that?
 
I’d prefer to have tado for each zone, how would I go about doing that?
Buy another Tado and then it would be wiring alterations. I/we can guide you, but would need photos of wiring center and existing thermostats.
 
Great, if I can get the down stairs working first then I’ll add the other Tado when I pick one up.

I’ve disconnect the receiver until I could get some clarity.

Both danfoss thermostats are wired as pictured
 

Attachments

  • IMG_6525.jpeg
    IMG_6525.jpeg
    269.2 KB · Views: 16
The Tado’s will need permanent lives and permanent neutrals in the wiring center, then, what you need to do: that black will go to the brown of the motorised valve in the wiring center - this is the switch live for the Tado. The common (Com) is the brown. Trace these in the wiring center - whichever motorised valve is opened using the downstairs thermostat will be the black for the Tado. Then the brown can go to Com.

No alterations are made at the boiler as that comes from the switch live out of the motorised valves.

Hope this makes sense
 