Texecom Bell duration

Joined
19 Jun 2019
Messages
94
Reaction score
0
Country
United Kingdom
The jumper in the wireless bell on my Premier Elite 64 is set to 15mins.

Within Wintex Global options there is an option to change this. If the duration is changed within Wintex, but not the jumper, will the duration change from 15 mins without changing the jumper,

Thanks

Dave
 
Sponsored Links
without testing it I honestly don't know but suspect not.

the bell duration was originally designed to keep the bell trigger output active for the duration of the timer.

with the wireless bell set at 3 minutes and the timer set at 15mins, the wireless bell will only ring for 3 minutes (not 15) but hard wired bells will fire for 15.
 