Yes, connect one of the multimeter probes to the terminal where the valves blue wire is,
and put the second multimeter probe into the terminal where the brown wire is connected.
If it reads 240V the actuator is faulty.
Make sure the meter leads are in the correct sockets on the meter, 1 lead in COM and the other in the terminal marked V.