TD RCD TT incomer surely
DM
We routinely use time delayed RCDs in commercial buildings where you have sub-mains or subsidiary distribution boards, The local board is protected by a 30mA standard RCD, the cable between the main board and the sub board is protected by a 100mA time delayed RCD, this gives a degree of protection by ADS (automatic disconnection of supply) to the cable whilst the standard RCD protects the final circuits.
No, live in a town, it's a large Victorian home, rewired 15 yrs ago. it has 3 boards as was a B&B so lots of elec shows, water heaters etc. When u say a picture, u mean map of where it is?... kitchen is a rear of house, 12m from porch where the mains in/boards are.To the OP - do you live in rural area or know if your earth is achieved by means of an earth rod. A picture of your mains position would be useful
but it has saved life once when a caetaker hacked through a 25mm2 SWA thinking it was dead - by rights it shouldn't have saved him but it did.