Towel radiator heating up when hot water is on??

Joined
27 Jan 2005
Messages
21
Reaction score
0
Country
United Kingdom
Hi, I've just moved into my new house and have noticed that when the boiler is set to be heating up the water in the cylinder, my towel radiator in the bathroom gets hot at the same time and the hot water coming out of the tap isn't as hot as I think it should be??
It only seems to be the towel radiator that heats up and it is a conventional boiler with a cylinder in the airing cupboard.
Any advice would be greatly appreciated.
 
Sponsored Links
It was common to pipe the bathroom rad parallel to the cylinder 50 years ago.
 
My house was only build about 20 years a go - the rad's in the 2 bathrooms are both plumbed in via a T-off between the boiler and circulation pump.

On my list of things to do is to pop a valve on at that point with a timer operated from the bathrooms so you can have the towels warming while in the shower and no need to heat them 24/7. They kinda stay warm by convection from the residual heat in the boiler, until the water or central heating call - then they get hot.

Might also be used as a pressure relief circuit to protect the circulating pump - I'll have to build in a valve for that too I guess..........

*please confirm this seems plausible, someone!*
 
Sponsored Links
Hi, I've just moved into my new house and have noticed that when the boiler is set to be heating up the water in the cylinder, my towel radiator in the bathroom gets hot at the same time and the hot water coming out of the tap isn't as hot as I think it should be??

Many houses in the UK have the bathroom radiator connected to the circuit serving the hot water cylinder. The intention is to allow the bathroom radiator/towel rail to be heated when the heating system is off in spring and summer. The bathroom needs additional heating since you'll be undressed and wet.

The towel rail can act as a short-circuit, starving the cylinder of heat, in which case you'd need to adjust the lockshield valve that should be on the return. The cylinder may be scaled up and/or it may be old and ineffective, and/or the boiler flow temperature may be too low. Probably best if you found someone competent to look at the system.
 