I have one of these titled units, manufactured 2018 and installed 2023. It has developed a problem of being uncomfortably hot even on the lowest economy setting. We've measured incoming water flow at about 12L/min relatively stable and about 10 degrees celsius so I think we can rule out the incoming water supply. Here's the issue and it is completely reproduceable every time the shower is turned on:

1) Turn the shower from OFF to FULL (5.6kW + 2.8kW elements both energised) with temperature dial on lowest. Flow output builds up to 5L/min, and will drop to 3L/min when dial is moved to max heat and then back up to 5L/min if moved back to min heat (i.e. behaves as expected).

2) Turn the element setting from FULL to ECO (5.6kW element energised) with the temperature dial on lowest. Flow initially starts at 5L/min, but slowly drops over about 1 minute to 3L/min (e.g. behaves as if you've moved the temperature dial to maximum). After this point it gets uncomfortably hot and adjusting the temperature dial makes no difference to the flow rate or temperature.

3) If you turn the shower from FULL or ECO to COLD the same drop to 3L/min is observed.

4) The shower continues to behave this way until you turn it back to FULL with lowest temperature dial, at which point the flow rate increases back to 5L/min and the temperature starts responding to the dial as you would expect.

I've never seen a failure mode documented for this unit where the flow rate is inappropriately decreased but only on the ECO and COLD settings. I have another identical potential donor unit with damaged casing, but that one was described to me as having an issue with temperature cycling cold and hot repeatedly (i.e. one or more parts in there is also faulty) so I am wary of trying to replace parts willy nilly and potentially stripping screw threads etc. Anyone know the best place to start?

Thanks very much
 
Solved it, it was the thermostatic flow control valve. After replacing it with the one from the donor I now have pressure back on COLD and the lower setting of ECO. It was still a bit warm for my other half, who likes a cold-but-not-freezing shower, so I swapped the microswitches for the heating elements around (meaning the 2.8kW element is the only one engaged on ECO, not the 5.6kW element). Perfect now, temperature floor is a lot lower, there's a bit of a gap between ECO->max and FULL->low but we are much happier with it!
 
Spoke too soon unfortunately, fault has returned, something seems to be sticking again. Presuming my donor unit doesn't have a faulty part with an identical problem, the only things I haven't tried are the solenoid and heater can, so will be trying those next.
 
I've now replaced every part of the unit with every part of the donor one by one, and the fault of low pressure on ECO/COLD is still there. At this point I have to imagine this is either expected behaviour (why would Triton design a shower that runs COLD on the lowest pressure??) or I have two units with an identical fault mode. Either way I think I am just going to replace the unit as I have no idea which way is up at this point.
 
I have one of those showers (but 9.0kW), it's quite easy to test the solenoid coil resistance without even taking off the shower cover, switch out (down) the shower RCBO/RCD, ensure pull cord switched on and press the shower start button then check the resistance between the (RCBO) load side L&N, a healthy coil should give 3K to 4K ohm resistance, mine is 3.67K (3,670) ohms. Don't forget to press the shower start button again and switch off the pull cord before switching the RCBO/RCD back in after the test.

The mains temp here just now is 22C so on your NOW economy setting of 2.8kW, a flowrate of only 2.23LPM should maintain a showering temp of 40C, the flowrate will have to fall to 1.43LPM to trip the TCO (selfresetting first stage) at 50C, those numbers are 6.76LPM & 4.35LPM at the full power of 8.5kW.

To rule out any hose restrictions, run it with the hose completely removed from the shower outlet.

I would also remove the mains inlet at the shower inlet and measure this flowrate, this will rule in/out a shower problem.
 
Last edited:
For Info.
Just carried out my yearly check of shower (9.0kW, T80Z), filter clean, flowrate test. & terminal connections. My mains pressure is now only 2.2Bar static which results in a max shower (upstairs) flowrate of exactly 6.0LPM. The heating can element resistances are (Eco) 9.4ohms & 16.3ohms to output 5.88kW & 3.25kW, total, 9.13kW, @ a nominal 230V, this means that the flow temperature with full power is 43.8C (from a now mains temp of 22C), this is too hot for me, so I have to run on the Eco element only and reduce the flowrate to 4.68LPM to give a showering temperature of 40C, a flowrate of 7.27LPM would be required to run at 40C and require a static head of ~ 3.6Bar which I had for over 40 years. I will now have to wait until the mains temp falls to 18.2C to allow full power usage at 40C at a flowrate 6.0LPM.
 
Here are a few photos of a old Mira shower stabilization valve, the valve is (in photo) just hanging from a piece of fishing line.
This valve is incorporated in the flow (temperature) control valve and I think the water pressure just pushes the spring loaded valve open a certain amount based on the differential pressure across it..... depending on the opening of the flow control valve, there is still a minimum annular space around the (stabilization) valve when shut.

Also, on my own and two other Triton T80Z that I've installed for relatives, a minimum of 1.15bar (at the shower) is required to close the microswitches, they will then reopen at ~ 0.75bar, at 1.15bar, the flowrate is only ~ 6.5LPM, despite both Triton (and Mira) stating that 1.0bar pressure should give a flowrate of 8.0LPM on a 9.0kW shower.

One very good feature of my old Mira Sport was that the microswitches would close with a tiny head pressure of ~ 0.4bar as I could and did run this shower on its Eco setting when fed from the CWSC during prolonger daily mains outages a few years ago, it would give a flowrate of ~ 3.5/3.8LPM. I don't know if this was the design of the shower or a faulty pressure switch, if faulty, then I would think it was faulty from day 1.
Based on the above, a Mira Sport (or the like) just might be a better choice if mains pressure is lower than say 2.8bar and the shower is installed upstairs. Personally, I would install a pumped shower if the mains pressure is less than 3.0bar, static.
 

Attachments

  • Mira Stabilization Valve1.jpg
    Mira Stabilization Valve1.jpg
    207.9 KB · Views: 67
  • Mira Stabilization Valve2.jpg
    Mira Stabilization Valve2.jpg
    213.8 KB · Views: 50

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top