Norcon, thanks for the insight which has certainly made me think. Do your comments apply to thermal stores in general or to the Chelmer Thermocat in particular?
I can see what you are driving at but you seem to be assuming that thermal store thermostats do not have any hysteresis. My understanding is that the Thermocat lower (ie UFH) stat can be set to fire the boiler at <=40C and cut it off at >=50C. Assuming about 140L of water in the lower half of the store, and assuming that water has a thermal capacity of 0.001KWH per L per 1C (my 3KW jug kettle takes ~2' to boil 1L of very cold water), then the boiler will deliver 1.4KWH to the store in one cycle. My new Grant Vortex boiler is rated at 23KW so this should take it about 4 minutes. If the UFH or DHW demands hot water at the same time then this period will obviously be extended beyond 4' but I cannot see what might reduce it.
In the case of the Grant boiler it condenses up to 55C according to its spec so with the UFH stat set to cut out at 50C the boiler will never be asked to operate outside its condensing range by the UFH.
Of course the DHW may be another matter but in our case the DHW demands should be relatively minor.
As stated in my previous post we are still some way off finding how it all works out in practice.
I can see what you are driving at but you seem to be assuming that thermal store thermostats do not have any hysteresis. My understanding is that the Thermocat lower (ie UFH) stat can be set to fire the boiler at <=40C and cut it off at >=50C. Assuming about 140L of water in the lower half of the store, and assuming that water has a thermal capacity of 0.001KWH per L per 1C (my 3KW jug kettle takes ~2' to boil 1L of very cold water), then the boiler will deliver 1.4KWH to the store in one cycle. My new Grant Vortex boiler is rated at 23KW so this should take it about 4 minutes. If the UFH or DHW demands hot water at the same time then this period will obviously be extended beyond 4' but I cannot see what might reduce it.
In the case of the Grant boiler it condenses up to 55C according to its spec so with the UFH stat set to cut out at 50C the boiler will never be asked to operate outside its condensing range by the UFH.
Of course the DHW may be another matter but in our case the DHW demands should be relatively minor.
As stated in my previous post we are still some way off finding how it all works out in practice.