Tundish connection

Joined
9 Mar 2011
Messages
66
Reaction score
0
Location
Hertfordshire
Country
United Kingdom
73 a9 aa 03 e3 71 28 c8 e6 a0 c0 e1 d5 25 e4 75 34 8b 0c 41 74 da e2 42 28 a9 fc 5f c2 bb 6a 8c 90 91 05 54 bd 7b 8c 26 42 b5 15 99 6f 4f 03

d2 44 4b d6 75 87 81 2d 6e 1b 41 92 dc 01 e7 a3 40 f2 30 29 99 d8 c5 82 54 45 04 43 fb a4 62 68 8a d2 b8 8a 64 dd

e5 a7 d2 b6 14 8f a3 8a 2a dc 84 ed 04 1d 8d ba 80 34 e1 08 d8 00


d8 4b e3 11 62 e9 f8 f7 21 4d 70 37 b4 52 55 67 ed 79 d9 a1 e8 d7 1c 4f c5
 
Last edited:
Sponsored Links
As Dan says, you should be G3 Registered to fit this, and the installation is notifiable to Building Control

1) The tundish is a safety device which allows the PRV to operate correctly even if D2 is blocked. Not installing it constitutes omitting a safety feature, which I'm sure you don't want to do...

2) Yes. If you'd done your G3 qualifications (or even RTFM) then you'd know ;)
 