Turbomax plus CH cones on for 10 seconds then F22.

Joined
31 Dec 2022
Messages
8
Reaction score
2
Country
United Kingdom
Boiler starts up, runs for 10 seconds then stops. Actions taken, check and cleaned pump head. ( does run and no debris in inpeller) isolated all but two rads which are i know are clean and tried running and have sentinel x800 the system, when it initially happened i did give the pump a little clout and it worked for a day, then it now never runs for more than 10 seconds and then does the F22 or ocxasionally f24 error coded. I think that leaves debris in PHE or faulty pump, NTCs, PCB or powerflush needed. Any ideas guys, have i missed anything, Next step is engineer but just posting this first for any reaction. Many thanks, HNY!!!
 
Sponsored Links
If I have the correct model ,above the pump is a micro switch that should make and break when pump starts/ stops is this happening
 
Sponsored Links
Some boilers detect the pump running when they sense a rise in pressure, watch the boiler pressure when it starts up and see does it rise by say 0.25/0.5bar.
 
thank you for your reply, no change on pressure gauge whatsover.
 
Sorry, should have been more specific, the model is 824e
 
Thanks, should have been more specific, removed the x800 after a day.
 
  • Thanks
Reactions: CBW
I have now established that the pump is not running when boiler fires up and dont think its capacitor as still doesnt run with a nudge. Cant ascertain if pump is receiving voltage but believe so as boiler goes through all other motions correctly then cuts out after 15 secs with f22.
 