Yeah its actually how it's done in my own house with red and black sheathed singles, but I've never done it myself.I think it used to be a common way of wiring the 2-way switching of the landing light.
Yeah its actually how it's done in my own house with red and black sheathed singles, but I've never done it myself.I think it used to be a common way of wiring the 2-way switching of the landing light.
And guess where that additional terminal often ends up...I did come across one case where someone had missunderstood their electrician friends advice and did not use twin and earth on either switch on a two way switch circuit but instead run a 3C & E from the rose to switch 1 and also a 3C & E from rose to switch 2.
My intial gut reaction was to think "No that`s wrong!" yet I soon realised no it was not wrong and could indeed it would work that way but you would need an extra choc block/crimp/wago in the rose and slight alterations to the rose connections yet only one 3 core to each switch and no T & E to either .
So if anybody actually does that way should we nominate that as say " 2nd option version B" and classify the one you`ve already mentioned as version A ?![]()
One benefit of the 3 core (& E) cable between the two switches method is if anyone has an Induction loop hearing aid it used to be a lot less chance of imparing usage of that hearing aid
Yes you are probably correct - I added that observation for a bit of completeness to the item I wrote as well as the mention of the 2nd option version B" I had seen and initially debated with myself.This is an issue in some cases, but I don’t think it applies to any of the circuits described in this thread.
If I got you right on that one Pete isn`t tht the one I called version B ?Or take s 3 core from the light to each switch and do the connections at the light.
There's also an alternative version of the second drawing, by using 3 core and e from the rose to the switch and 4 core and e between the two switches, you can have a Neutral at each switch
Then you have the means to supply a light direct from either switch or fit fancy switches that require a Neutral
Yes correct but is 4 core & E readily available as such?There's also an alternative version of the second drawing, by using 3 core and e from the rose to the switch and 4 core and e between the two switches, you can have a Neutral at each switch
Then you have the means to supply a light direct from either switch or fit fancy switches that require a Neutral

Later, some such houses would have been rewired (pre RCDs) with separate lighting circuits upstairs and down, and no one would have realised that there was now a "borrowed" neutral, i.e. the live feed for the landing lights came from the ground floor lighting circuit, but the neutral was from the first floor lighting circuit.
Err not sure, I think you meant a 3 core between switches, I meant a 3 core from the light twice so you end up with 1x 3 core at each switch.If I got you right on that one Pete isn`t tht the one I called version B ?
Thinking about it proberly not, it was long ago I did it and i may have used 2.5mm it was flat like twin and earth i assume it was used for 3 phase and neutral from a job somewhereYes correct but is 4 core & E readily available as such?

It was often done in houses where there would be switches near the bottom of the stairs for the hall and landing lights and one near the top of the stairs for the landing light.The first way seems a bit more awkward to me, I think it was done more years ago when they used to use sheathed single cables.
I've never done it in a house, only when wiring in conduit.