UFH flow temp

Joined
17 Feb 2008
Messages
694
Reaction score
11
Location
Berkshire
Country
United Kingdom
I have a 3 port ufh manifold, taking temp of all flow and returns, the 1st on manifold has a flow 4 degrees lower than other although return is similar, tried playing with valves but still cant get flow up to near others, any thoughts?
 
Sponsored Links
Blockage or air in the loop. You could try flushing the loops through and see if it improves. Don't use the boiler fill. You'll need to connect a hose a per instructions for your manifold.
 