Hi

I have a leaking JG blending valve on my UFH

The leak is on the upstairs manifold (the second manifold being downstairs)

What is the correct procedure for changing the valve body ?

? Should I isolate both manifolds with the valves then turn the water off and drain ?

Thanks for any input
 

Attachments

  • WhatsApp Image 2026-03-24 at 11.19.13 (1).jpeg
    WhatsApp Image 2026-03-24 at 11.19.13 (1).jpeg
    167.8 KB · Views: 24
  • WhatsApp Image 2026-03-24 at 11.19.13 (2).jpeg
    WhatsApp Image 2026-03-24 at 11.19.13 (2).jpeg
    164.5 KB · Views: 24
  • WhatsApp Image 2026-03-24 at 11.19.13.jpeg
    WhatsApp Image 2026-03-24 at 11.19.13.jpeg
    161 KB · Views: 23
Are both manifolds serviced by the same Blending valve and pump assembly? Normally there would be one for each.

You will need to isolate the manifold and valve/pump assembly from the CH system and depressurise the UFH before it can all be disconnected.
 
@Madrab Thank you !


If anyone comes across the same problem you can buy just the headwork for the valve here;

As suggested aboved close the manifolds, turn the water off and drain the taps at the lowest level then swap over
 