Hi All
Went to see customer with an UFH problem. Pump not working so replaced, but still no heat! Have heat to manifold via open 2 port motorised valve. Heat starts to enter UFH pipes but does not flow through to return manifold. System has 2 auto air vents but cannot get any air out. Have tried attaching hose to return manifold to purge some water and hopefully some air but no joy! System has 2 loops each controlled by its own stat and TRV. Have removed heads from trv's to see if they are stuck etc. Still no flow. I am assuming its an air problem but any advice would be appreciated.
Cheers
Went to see customer with an UFH problem. Pump not working so replaced, but still no heat! Have heat to manifold via open 2 port motorised valve. Heat starts to enter UFH pipes but does not flow through to return manifold. System has 2 auto air vents but cannot get any air out. Have tried attaching hose to return manifold to purge some water and hopefully some air but no joy! System has 2 loops each controlled by its own stat and TRV. Have removed heads from trv's to see if they are stuck etc. Still no flow. I am assuming its an air problem but any advice would be appreciated.