unvented system inlet pipe

Joined
11 Dec 2007
Messages
95
Reaction score
0
Location
Essex
Country
United Kingdom
I have booked to go on unvented training day

but I have been asked to price putting in a unvented tank

the work will not be done till I have done the training but so I can price the job right can any one tell me if the inlet pipe on a 300L mega flow can be in 15 mm I can not seam to find any info on it

my standing press is 4.8 bar
and the flow rate is 14 letters a min

is this ok
only running a bigger pipe from the mains is very very hard and the stop cock is 15 mm

thanks
 
Sponsored Links
14 ltrs a min is useless for a megaflow anyway, are you sure you're measuring it right?
 
sooey....i agree....measure again.

not normal (in leicester anyway) to get such high pressure and low flow)
 
Sponsored Links
i used a flow cup that I got of e bay and had no paper work

Where do you take the reading from
I took it that where the water comes out the side that s your flow
 
HI

15mm for 300l tank no good .minimum 22mm inlet pipe required.common sense.
 