Upstairs radiators heat up when HW is on

Joined
30 Apr 2007
Messages
3
Reaction score
0
Country
United Kingdom
The upstairs radiators in my house heat up when i have the water heating on. The heating system is about 15 yrs old, someone has said to me that the y plan valve needs to be replaced. Is this correct and how do i do it?

Chris
 
Sponsored Links
Can you feel the heating pipe out of the 3 port valve getting warm when h/w is on?

Indeed have you got a 3 port valve or is this just what someone has suggested out of the blue :rolleyes:
 
the pump is in the airing cupboard (above the stairs) with the "mid position actuator". The 3 pipes that go into it all heat up when i put the hot water on. Its got a little push in button that doesn't appear to do anything on the side and a button that slides on the end - what do these do?

I bought a SUNVIC 3-port motorised valve this morning, it has a dial on the end that will turn and moves a plate inside. Iwas wondering if this was a manual overide in case the motor broke but it doesn't go far enough round to cover either of the holes.
 
Sponsored Links
yes the 3 port valve would cause the upstairs rads to get hot as it prob stuck in the mid position. the little black button would be for removing the head on the valve. i would buy a honeywell 3 port and just replace the excisting valve, sounds like a danfoss valve.
 