That's no different from the modern RCD, which is a current-operated ELCB by a different name. All that's happened is that it's undergone a couple of "official" name changes over the years, and the types installed today for general protection are more sensitive.That a shock could still be suffered and the unit would not trip.
any parallel paths to earth such as the water / gas mains (if they are metal) via protective bonding can render a VOELCB useless.
It would do it's job in the sense of operating if the pd between the installation's CPCs and earth electrode was 50V (or whatever) or more. However, if (as in my installation) the resistance of the path to earth via parallel paths is much lower than via the earth electrode, then it's surely very possible for a lethal current to flow through the victim to earth (via parallel paths which are partially bypassing the coil) without the voltage across the ELCB coil rising to anythong like 50V?You could have as many parallel paths to earth as you liked on the frame (installation) side of the coil, but so long as everything connected to the electrode side was completely outside the influence of those items, the ELCB would still do its job.
These are earthed, and the tank can have an earth path back to the mains cold pipe.
That was the maximum permissible voltage under the worst conditions, but in practice the actual tripping voltage was often considerably less. One of the popular Crabtree types had a 500-ohm coil which was designed to trip the mechanism at a coil current not exceeding 35mA. It was specified for use with an earth electrode of up to 500 ohms. There was obviously a fair margin for electrode resistance increase built into that calculation, since even at that earth resistance the ELCB would trip at 35V maximum. If it was used with an electrode with, say, a resistance of a more modest 200 ohms, then the tripping point would be reached a little below 25V.The key point with VOELCBs was that as soon as the MET voltage raised above a set voltage above true earth they tripped, possibly 50v??
Certainly, but remember that the voltage-operated ELCB was never designed to try and protect against such things. It's sole purpose was to prevent the internal earthing system of the installation from rising to a dangerously high potential in the event of a fault which could not be cleared by regular fuses or circuit breakers due to the relatively high loop impedance.However, if (as in my installation) the resistance of the path to earth via parallel paths is much lower than via the earth electrode, then it's surely very possible for a lethal current to flow through the victim to earth (via parallel paths which are partially bypassing the coil) without the voltage across the ELCB coil rising to anythong like 50V?

Sure, but did they not have ('main') bonding in those days? Provided one had an equipotential zone, the one thing these devices were designed to protect against was something which shouldn't happen, or be a risk to human beings - there's no risk (to human beings) in the internal earthing system of an installation (i.e. CPCs and exposed-conductive parts) rising to a 'dangerously high potential' relative to true earth if true earth potential does not exist within the building.Certainly, but remember that the voltage-operated ELCB was never designed to try and protect against such things. It's sole purpose was to prevent the internal earthing system of the installation from rising to a dangerously high potential in the event of a fault which could not be cleared by regular fuses or circuit breakers due to the relatively high loop impedance.