In winter I set the boiler d0 to 30-38kw, dependent on how cold it is. the pump is set to proportional curve at 8m.
In spring I set the d0 to 15kw as it's only heating the 300l water tank. I noticed the boiler often cycles constantly waiting on the pump and it can take over an hour to get the tank to any decent temperature as its cycling every 30-60 secs at worst.
I've set the pump to constant curve with a 5.5m and this seems to get the water pushed out much better to allow the boiler to stop cycling and modulate. It then heats the tank in 10-20mins
The manuals for the pump are not very DIY friendly, I read proportional pressure works well with TRV's, I presume that's why it doesn't work so well when the rads aren't on and it's only heating the tank.
What would you all recommend, setting constant curve in the spring, alongside the d0 at 15kw and reverse it in winter, or just leave the pump at constant curve with 5 or 8m the whole time?
13 rads, 5 towel rails ,UFH in one large room and 300L hw tank.
Thanks
In spring I set the d0 to 15kw as it's only heating the 300l water tank. I noticed the boiler often cycles constantly waiting on the pump and it can take over an hour to get the tank to any decent temperature as its cycling every 30-60 secs at worst.
I've set the pump to constant curve with a 5.5m and this seems to get the water pushed out much better to allow the boiler to stop cycling and modulate. It then heats the tank in 10-20mins
The manuals for the pump are not very DIY friendly, I read proportional pressure works well with TRV's, I presume that's why it doesn't work so well when the rads aren't on and it's only heating the tank.
What would you all recommend, setting constant curve in the spring, alongside the d0 at 15kw and reverse it in winter, or just leave the pump at constant curve with 5 or 8m the whole time?
13 rads, 5 towel rails ,UFH in one large room and 300L hw tank.
Thanks