A generous plumber neighbour sorted the F28 fault on our boiler which was a frozen condense pipe as suggested by two forum users.

But we now have another problem.

The pressure was fine when we restarted it, having cleared the condense pipe. But now it is much too high - right in the red range so we had to turn it off. Tried bleeding the rads to lower it but it climbed back up.

Could there be something our neighbour forgot to do when resetting things? We are really reluctant to call him out again. He did us a favour and we don't know him very well.

Any suggestions welcome as we have had to turn the boiler off.
 
Sponsored Links
Joined
26 Jun 2004
Messages
64,092
Reaction score
4,620
Location
London
Country
United Kingdom
You should know how to increase the pressure.

Either two screws under boiler or a seperate filling loop with silver braid ( or both ).

That may have been left party leaking.

Ask him where it is if you dont know.

Tony
 
Joined
21 Dec 2010
Messages
7
Reaction score
0
Location
Hertfordshire
Country
United Kingdom
Hi Tony
Thanks for posting. I know how to increase the pressure. I need to know how to decrease it. I did it by bleeding the radiators but it just keeps climbing back up.
 
Joined
19 Apr 2005
Messages
454
Reaction score
38
Location
Gwent
Country
United Kingdom
Looks like you have left the filling valve open,and water is still entering the system,hence the pressure is still rising ;)
 
Joined
2 Nov 2010
Messages
3,423
Reaction score
515
Location
Humberside
Country
United Kingdom
Sounds like the filling loop is open or passing and allowing more water into the boiler/central heating.
 