• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Vaillant Combination Boiler

Joined
12 Mar 2005
Messages
2
Reaction score
0
Country
United Kingdom
Central heating OK, hot water OK, but bar gauge only reads 0.5 and drops to 0 when hot water turned on.
Handbook recommends minimum bar 0.8, how do you raise this pressure.
Boiler less than 10 years old, either type242/1E or 282/1E
 
Just top up the water, you should find the filling loop very near the boiler. It usually looks like an armoured flex hose about a foot long going from the mains (15mm) to the heating return (22mm)
 
It's a Vaillant, you might need the little silver key if it's got an integral filling loop (Turbomax Plus).
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top