vaillant ecomax 824e no hot water

Joined
5 Sep 2004
Messages
14
Reaction score
0
Country
United Kingdom
hi ive had the above boiler for aprox 3 years
recently when running hot water .it goes hot then drops to warm only on reseting boiler does it go hot again for a short while then goes warm to cold looking at fault codes it says f25 althouth i cant finf 25 in manual
any help .ill be gratful thanks
 
Sponsored Links
What kind of reset are you doing?

Can you measure the flow and return temperatures on DHW ?

Tony
 
thanks for geting back im switching boiler on and of looking at the tempersure on the panel the temp rises then after a short while falls to about 6o d eg from about 80 deg
 
Thats not what I asked!

But if its going up to 80°C then that rather indicates the plate HE is blocked as usual because the system was not properly cleaned at installation.

Tony
 
Sponsored Links
sorry can you tell me how to check for flow and return temperatures on DHW thanks
 
You need a contact thermometer and put it on the flow and return pipes from the combustiion chamber.

Its the difference we want and a differential thermometer is most ideal.

Tony
 
thanks for geting back looking at the forum
simular prob apear to be a diverter valve any thoughts on this
is this a hard job to change thanks
 
I was trying to help you DIAGNOSE the problem.

I could hardly go to a client and change parts at his expense if I was not sure they were the problem.

As you dont want my help to diagnose the problem then you had better change the diverter valve instead and hope thats the problem! They must be easy to change as I can do a few every month!

Tony
 
Doesnt sound like diverter but to test turn ch off and allow ch to cool down. Open hot tap and check ch flow pipe 12" or so from boiler. If it rapidly gets hot then the diverter is probably at fault.

I however think agile is barking up the right tree with blocked heat exchanger. I have changed / cleaned many of these due to blockages on vaillants
 
hi i am very sory if i upset you i do need your help any comments or advice iwould be very gratfull i mensioned the valve as i just hapened to notice some one on here with a simular prob thanks for geting back
 
thanks for your reply is the flow pipe one of the copper pipes under the boiler .what you are saying is that some of the heat is going to the rads rather than hot water .if its the heat exchange is that a job a diy can do thanks
 
Yes its one of the 22mm pipes, the one on the left as you look at it iirc.

The heat exchanger can be done DIY, just take your time and follow manuafacturers instuctions
 
You don't need surface/pipe stats for this.

D40 is the flow temp and D41 is the return temp.

D3 will give the actual HW temp leaving the plate HE.
 
thanks for everyones help here are the setings as i can see them
D3 37 . D5 66 . D7 60. D40 63. D41 41
THESE ARE SHOWING WHEN HOT WATER TAP IS RUNNING
ANY HELP TO SORT THIS OUT IS VERY WELCOME THANKS
 
Forget about D5 and D7.

When the HW tap is running does the ch flow pipe get hot?
 