Wiring fault or plumber may have tempered with fan speed (dependant on skill) and turned it up instead of down. Fan speed settings are back to front, up is down, down is up. I had a vaillant engineer do this to me.
IMO respectively.
Wtf
Wiring fault or plumber may have tempered with fan speed (dependant on skill) and turned it up instead of down. Fan speed settings are back to front, up is down, down is up. I had a vaillant engineer do this to me.
IMO respectively.
I'd be looking at the pump first off. Check if the impeller is clear of debris and it is set to its highest speed.
Have you checked the feed tank in the loft. When you turn the dial on the front does the temp move?
Nathan
I don't know about royalty; but we know a hell of a lot more about boilers than you if you have managed to conflate the Pump Overrun Status code with fan speeds and wiring fault - based on a recollection from a Group Service visit.
D.0 seems about right.
Having it set too high can mean the boiler runs to hard shuts down and sits on S.07 until it times out and starts again.
Having a poorly adjusted by-pass - especially on a 4 series - or a guffed pump impellor will cause similar issues.
Wiring fault would be way down on the list of likely problems based on the information given.
To carry on we need to answer Emerlloyd's good question from page 1.
What controls have been used? More specifically the posher of Vaillants in house stuff. If you have a weather sensor fitted then the boiler will not run very hot in heating mode. Mine is programmed not to fire the burner when the outside temperature is above 20 degrees. It is then on a gradual slope to a flow temp of 55 degrees at -3 outside.
Have you checked the pump?
Have you checked your by-pass valve?
Make sure the pump is a 6 metre head unit and that the service valves are fully open.
It is unlikely that the fan speed is an issue .
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local