Err that's a thermostats job, if you are worried set the thermostat to min
.... logically it should be but all the Vaillant internal 12C protection thermostat does is circulate water within the boiler.
If the concern is there of the system being exposed to sub zero temps, then there is an established system standard for CH, designed to protect the whole system and is as described, a frost stat and pipe stat working in tandem that overrides the controller and starts the boiler. The boiler runs until the pipe stat registers 30Deg @ the return warming up the whole system then the boiler shuts down.
Fine for the heating circuit but even if this ran continuously since no flow in cold water feed or tap hot water outlet pipes these could still be frozen solid.
Ah, so to protect the hot water pipes to the outlets? If there is a risk of them freezing then they should be insulated. Are we talking about a property that would be left empty for an extended period of time over the winter? If that's the case then the recommendation and standard would be to isolate and hot and cold water supplies and drain them down and implement the system frost/pipe stat setup.
The installer has put standard grey lagging on all four pipes - cold water feed, tap hot water output, central heating output, central heating return.
Primarily simply talking about the overnight temperature dropping to say -10C and daytime temperature only 0C. Back to 1980's overnight dropped to around -20C, low enough for diesel to become too thick for vehicles to run.
Even if alarm was set to wake up every 2 hours and run tap hot water the cold feed water would be close to freezing so potentially not take long to freeze.
If daytime temperature was only 0C or didn't even reach 0C cold feed and hot tap outlet could freeze during the day even if heating pipes stayed above 0C because house thermostat intermittently kicked in.
Leaving the property unattended is scenario I had not thought about. With a combination boiler can the water stop tap be turned off and a both a cold and a hot tap opened to at least partly drain the pipes then left open so a volume for remaining water to expand yet the boiler be left on and the house thermostat set at 5C or even 10C? Or would the boiler lockout in a fault condition because the cold water feed pressure was zero?
I still see fitting trace heating wire with the thermostat on the cold feed pipe as the best / safe option. So long as it keeps the pipes, lagged remember, above 0C, which I presume is how it is designed and and rated, then the freezing risk is eliminated so long as the boiler looks after itself and the house thermostat set at say 10C keeps the internal pipes all above 0C.
Just putting the trace heating wire on the cold feed and tap hot water outlet would probably suffice given the heating pipes have to drop to 0C but a 10m kit is £50 and a 20m kit is £78 so might as well cover all 4 pipes. Since the cable is self regulating if the heating pipes are warm much less heat would be added to them than the cold feed and tap outlet pipes. Two kits are another option but more cost and need two wall sockets as for what is a permanent installation using a 2-way splitter or extension lead even if only 0.5m long not a good idea and reduces reliability.