Good afternoon all, first post here
My seven year old boiler started giving DHW problems some time ago.
Took of DHW heat exchanger, de scaled - lightened it noticeably - then refitted. Improvement but not back to as new, intended to renew next time it happened..
Started playing up again ( luke warm showers) so fitted a new OE exchanger, but was disappointed with the result.
Took forty minutes to run a just warm bath.
Water temp touches 70 deg C indicated with cold water choked down a bit to a flow rate of 8 l/min., temp just OK for a shower but it won't reach the 80 degrees mentioned by others.
Diverter valve OK, no bleed over to heating side at all.
d.40 shows 67; d.41 shows - .
Thinking this might be DHW temp sensor, other than this, in heating mode runs sweet and is powerful.
All suggestions welcome and appreciated.
My speciality is brickwork, general construction, building regs and construction defects and inspections so look forward to replying to posts where appropriate elsewhere.
Best wishes
My seven year old boiler started giving DHW problems some time ago.
Took of DHW heat exchanger, de scaled - lightened it noticeably - then refitted. Improvement but not back to as new, intended to renew next time it happened..
Started playing up again ( luke warm showers) so fitted a new OE exchanger, but was disappointed with the result.
Took forty minutes to run a just warm bath.
Water temp touches 70 deg C indicated with cold water choked down a bit to a flow rate of 8 l/min., temp just OK for a shower but it won't reach the 80 degrees mentioned by others.
Diverter valve OK, no bleed over to heating side at all.
d.40 shows 67; d.41 shows - .
Thinking this might be DHW temp sensor, other than this, in heating mode runs sweet and is powerful.
All suggestions welcome and appreciated.