Just want to check I did the right thing, as its possible that the mrs turned the wrong tap on in an attempt to find a stop cock on a house I just purchased.

The pressure indicator showed over pressure and the display was flashing 4.6 bar. according to some searching this might be due to a fill loop being left open. I bled about a bucket of water out of the rads and the pressure dropped to low end of red, but then returned to max within about 10 mins. I closed the tap on the green thing picture 3 and then bled about a pint of water out and the pressure dropped to img 2 and has stayed there. Is the bottom pic basically my fill loop? It wasn't quite as per the diagrams in the guide.

thanks for any help.

48584678326_e6d26717f7.jpg

48584824632_73a4a180e2.jpg

48584678261_014e073117.jpg
 
The silver ,braided ,flexible hose is your filling loop . The black handle opens / closes to allow water into the system.
If the pressure gets to around 3 bar ,the PRV should lift ,and release water out of the system ,so shouldn't get to 4.6 bar. Needs checking !
 
thanks - will get it checked. Had a chap booked, but we only use the place as holiday home and aren't always there so logistics meant couldn't find a day that worked

I take it the PRV is not user serviceable?
 
If it doesn't fully close,its usually in need of replacing ,sometimes opening and closing a few times may be successfull in clearing any foreign matter that may be preventing it from closing fully.
 