can any body please explain to me the calculation for determing the height of the vent pipe above a 50 gall cistern and the gap between the water level and the pipe.
 
Joined
3 May 2007
Messages
5,320
Reaction score
1,064
Location
Surrey
Country
United Kingdom
From the Water Regs G20.3:

"Where vent pipes from either a primary or secondary system terminate over their respective cold water feed cisterns they should rise to a height above the top water level in the cistern to prevent discharge occurring under normal operating conditions."

The calculation given is V = 0.04H + 0.15 where V is the height of vent pipe above the top water level and H is the height from the top water level to the cold water inlet to the hot water cylinder. V & H are in metres. This calc only relates to gravity circulation systems. If a circulation pump is installed due allowance should be made for induced head.

The end of the vent pipe must not be below the top water level in the cistern.
 
Sponsored Links
Joined
14 Jul 2007
Messages
2,176
Reaction score
478
Location
Cambridgeshire
Country
United Kingdom
The height to which a vent pipe is to rise above the water level in a cwsc is found by allowing
40mm for every 1m head of waterin the system
plus an additional 150mm

for ex the distance between base of boiler and the water level in a cistern is 5m,the vent pipe should be carried up above the water level by a min distance of

5x40+150=350mm
 
Joined
23 Mar 2008
Messages
24
Reaction score
0
Location
Berkshire
Country
United Kingdom
The height to which a vent pipe is to rise above the water level in a cwsc is found by allowing
40mm for every 1m head of waterin the system
plus an additional 150mm

for ex the distance between base of boiler and the water level in a cistern is 5m,the vent pipe should be carried up above the water level by a min distance of

5x40+150=350mm


THANKS TO YOU BOTH.
 