Robbie, blowing off at the PRV HAS to be done. How else are you going to know it operates correctly. As a heating engineer who solely repairs boilers, I use this component to drain the boiler. If it leak, well so it be- it gets replaced. It is a safety component that has to be tested when the boiler is serviced.
Drain the boiler to 0 pressure and pump up the expansion vessel AND keep draining the boiler until no more water comes out the vent. Keep pumping until EV pressure is at 0.7 bar. Now pressurise the boiler to 1.5 bar. Vent the white chamber (11mm spanner). Repressurise to 1.5 bar.