vokera combi rises to 3 bar and leaks water at prv outlet

Joined
12 May 2007
Messages
5
Reaction score
0
Country
United Kingdom
my boiler when switched on gradually rises from 1 bar to 3 bar and leaks water from the prv outlet. when i de pressurise system back to 1 bar and switch on the same happens, but otherwise the boiler appears to operate normally? any help would be appreciated
 
expansion vessel will need recharging

see FAQ
 
If expansion vessel has water squirting out of valve it is knackered!
 
Went to one a few weeks ago (a compact) and upon inspecting got a considerable amount of water out at pressure. Was about to book in for new one, but gave it another go to which it eventually stopped and then just needed a re-charge?

How that much water got in there in the first place? I know theres usually a dribble..
 
If water is there surely( I know you are Rob!!) diaphragm must be split or something :?
 
Must be able to develop slow punctures or similar! This was atleast 3 weeks ago and havent been back since.... :)
 
if you pump up an expansion vessel with a split bladder and the shroooders ( i really dont know how to spell it :) ) holds then it works

:)
 