Vokera Linea-- loss of pressure.

Joined
1 Feb 2007
Messages
3
Reaction score
0
Location
Yorkshire
Country
United Kingdom
My Vokera Linea is losing pressure rapidly when on heating. I've checked all my pipes and no leaks were found. On the outside wall, behind the boiler, there is an open ended 15mm copper pipe. I taped a plastic bag over it, put the heating on and when i came back 1 hour later the bag was full of water. Is there a valve that needs turning off or resetting?
 
Sponsored Links
sime10 said:
Pressue relief valve needs changing

After the expansion vessel has be recharged or the flexy pipe to it has been unblocked. ;)
 
Sponsored Links
Scatmanjohn, I though Scotland was Vokera country. What do columbians need vokeras for, surely not for production of coke.
 
I always knew there was money in drugs (be it what you smoke in a pipe or take for a sore head), god only knows why I took up (NG) gas sniffing
 