My parents are having poor performance from the central heating the radiators are only getting fairly warm rather than hot. They live in an old house with high ceilings so have 11 large radiators which with the recent cold weather has resulted in the heating being unable to get the temperature above 13c with the heating running 24 by 7.
If you watch the boiler in CH mode if fires up OK and heats the water to 80c where the burners then cut out and the output temperature drops down to around 30-35c then repeats the process. As it takes around 3 minutes for it to drop in temperature and less than a minute to reach 80c again I assume this is the reason the radiators are not getting hot as they are not getting a constant supply of hot water.
They have a BG contract who advised nothing is wrong with the boiler and that the system needs a power flush at £800. Rather than pay BG last week I drained the system refilled it with Sentinel X400 in the system and ran it until today, drained it again and then removed each radiator and flushed out with a hose pipe. There was a fair amount of sludge in the radiators but it didn't take too long to clear them and the water coming out of the drain outlet was clear both times I drained the system.
I have read a few posts on here that if a similar scenario happens with the DHW it may be a clogged up secondary heat exchanger (which looks tight to remove) however the hot water seems unaffected the boiler will sit at a steady 50c with the hot water tap running I did only run the tap for 3 or 4 minutes however. (They have a power shower so the hot water is never on for long periods)
I will run the hot water for longer tomorrow incase it may be a clogged heat exchanger is there anything else I can check before calling out BG again I suspect as I have flushed it out they are going to insist that they do it before looking at the boiler again.
If you watch the boiler in CH mode if fires up OK and heats the water to 80c where the burners then cut out and the output temperature drops down to around 30-35c then repeats the process. As it takes around 3 minutes for it to drop in temperature and less than a minute to reach 80c again I assume this is the reason the radiators are not getting hot as they are not getting a constant supply of hot water.
They have a BG contract who advised nothing is wrong with the boiler and that the system needs a power flush at £800. Rather than pay BG last week I drained the system refilled it with Sentinel X400 in the system and ran it until today, drained it again and then removed each radiator and flushed out with a hose pipe. There was a fair amount of sludge in the radiators but it didn't take too long to clear them and the water coming out of the drain outlet was clear both times I drained the system.
I have read a few posts on here that if a similar scenario happens with the DHW it may be a clogged up secondary heat exchanger (which looks tight to remove) however the hot water seems unaffected the boiler will sit at a steady 50c with the hot water tap running I did only run the tap for 3 or 4 minutes however. (They have a power shower so the hot water is never on for long periods)
I will run the hot water for longer tomorrow incase it may be a clogged heat exchanger is there anything else I can check before calling out BG again I suspect as I have flushed it out they are going to insist that they do it before looking at the boiler again.