Vokera Linea Max cycling endlessly

Discussion in 'Plumbing and Central Heating' started by Mark the Harp, 13 May 2018.

  1. Mark the Harp

    Mark the Harp

    Joined:
    14 Jun 2016
    Messages:
    13
    Thanks Received:
    1
    Country:
    United Kingdom
    Hi all! I hope there’s someone out there who can solve this mystery.

    I first noticed an issue a few days ago, because even in the hot weather, the radiators were getting warm.

    In either DHW or DHW+heating (makes no difference):

    Internal circulating pump runs constantly during which:

    - Boiler rests for 70s approx

    - Runs for 15s approx

    - Display reads temp which goes from 58/59 (resting) to 74 (during the 15s it’s heating).

    This repeats endlessly

    ———-

    Hot water demand instantly starts boiler, which then reads DHW temp (as it should) and hot water is as it should be.

    When DHW demand stops, boiler stops firing and returns to monitor heating water temp (as it should) but to endless cycling as above

    The radiators get warm (not hot but constantly warm).

    Calling for heat from thermostat seems to make no difference to the cycling and the boiler still doesn’t run for longer than 15 seconds - unlike what it would be doing if it was trying to heat up the radiators.

    Divertor valve motor is constantly energised with 240v (water to DHW circuit) throughout any of the above.

    I’ve already had a leaking filling valve replaced, together with a new expansion vessel and thermistor, so obviously I’ve thrown a bit of money at this thing. I just want to know if the new faults are something that’s also fixable, or whether I should just go for a new boiler. It’s quite a large house. Any replies appreciated!
     
    Last edited: 13 May 2018
  2. Sponsored Links
  3. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    10,976
    Thanks Received:
    2,148
    Location:
    Oxfordshire
    Country:
    United Kingdom
  4. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    4,910
    Thanks Received:
    848
    Country:
    United Kingdom
    Yes it is fixable.
     
  5. Mark the Harp

    Mark the Harp

    Joined:
    14 Jun 2016
    Messages:
    13
    Thanks Received:
    1
    Country:
    United Kingdom
    This is all positive! Any pointers as to what I should be looking for? Happy to look at any electronics / sensors etc.
     
  6. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    12,542
    Thanks Received:
    3,716
    Location:
    Lanarkshire
    Country:
    United Kingdom
    first thing to do is disconnect all external controls and see if it still does it.
     
  7. Sponsored Links
  8. Mark the Harp

    Mark the Harp

    Joined:
    14 Jun 2016
    Messages:
    13
    Thanks Received:
    1
    Country:
    United Kingdom
    Good idea. Will try that.
     
  9. Mark the Harp

    Mark the Harp

    Joined:
    14 Jun 2016
    Messages:
    13
    Thanks Received:
    1
    Country:
    United Kingdom
    Prior to disconnecting the external controls, fired it up this morning, and all sorts of strange noises. Banging and intermittent whooshing from the pump. I have a horrible feeling this thing is just about to die spectacularly so I think I may well just have it replaced.

    Thinking of the Worcester Bosch 550 – I have a Nest thermostat already. Fortunately we have another boiler upstairs which operates separately, so not without hot water.

    Cheers - good alternative boiler suggestions always welcome if there’s a better one for similar money than the 550.
     
  10. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    12,085
    Thanks Received:
    2,300
    Location:
    Glasgow
    Country:
    United Kingdom
    Your boiler needs a proper service
    Have yet had a need to replace this model
    Uncomplicated boiler easily fixed, if you know what you are doing.
    Not end user fixable as will need seals etc a good service engineer would have on hand
     
  11. Mark the Harp

    Mark the Harp

    Joined:
    14 Jun 2016
    Messages:
    13
    Thanks Received:
    1
    Country:
    United Kingdom
    Hi DP. What I’ll do is get the plumber who did the expansion vessel / thermistor / filling valve to come back and have a look. A new boiler would be a lot of money so if it’s fixable it’s a question of what would be cost-effective.

    Cheers
     
  12. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    12,085
    Thanks Received:
    2,300
    Location:
    Glasgow
    Country:
    United Kingdom
    The store is not getting up to temperature, hence boiler keeps firing
    That is why I said proper service and diagnostics
    If your plumber ( read heating 'engineer') is clued up on this boiler, he will know what to do. If not, he will be recommending a new boiler
     
    • Like Like x 2
  13. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Sponsored Links
Loading...

Share This Page