    Hi,

    I'm using wago connectors where possible to wire up my new light fittings (with metal casing).

    I'm using the 2-way / 3-way lever connectors for the supply/to switch/loop wires, and was hoping to use the 224 series connectors for everything else.

    However, a couple of my lights have more than 2 earth conductors. I used an old fashioned terminal block for one of them, but was hoping there was a wago solution for the other. Is there any reason why I shouldn't use a 5-way lever connector to connect all the earth wires together (including the one from the metal casing)? I think my existing light is likely to have 4 earth conductors, but not sure until I remove sleeving.

    Any other suggestions? Thanks in advance!
     
  2. Sponsored Links
  3. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,639
    Thanks Received:
    1,406
    Country:
    United Kingdom
    Nothing wrong with using 5 way wagos for earth conductors ,why do you think otherwise ?
     