Wait isn’t the NRV between the balanced cold and the UVC EV/cylinder feed? It’s what stops hot water going back into the balanced cold?I would suggest installing it before the PRV because the PRV closes when the upstream pressure is > 3.0bar so the arrestor wouldn't be of any benefit if installed on the balanced cold, (if the hammer is in the mains leg), the UVC EV should act as a arrestor to relieve the pressure in the balancedmaincold if this is where the hammer is occuring as the ICG NRV will then open in the UVC direction.