In the middle of a shower the water just stopped, what's wrong? The switch does go in and stays in.



20250624_212937.jpg
20250624_213037.jpg
 
Looks like there's no power, button should be lit.



Which button? Usually just the two led lights- blue and red, both look lot on photo above, don't they?

This is photo of isolating electric switch in cupboard behind shower- lights on


Where's the fuse?





Check the pull cord or outside switch and fuse.
20250624_215105.jpg
 
Either the shower unit is not getting a 230/240 volts supply ,or there is a fault within the shower ( possibly the solenoid).
You would need an electrical testing instrument to determine which it is.
 
Usually the MIRA's have a light on the power button, not sure with that one though, never fitted a Play.

If it is getting power to the unit then as suggested it'll be a component failure, like the solenoid.
 
Yes ,you can buy a new solenoid. But first you need to establish the voltage at the showers main terminal block between live and neutral is 230/240 volts.
The solenoids resistance can be checked with a multimeter to determine if that's at fault .
 
Yes ,you can buy a new solenoid. But first you need to establish the voltage at the showers main terminal block between live and neutral is 230/240 volts.
The solenoids resistance can be checked with a multimeter to determine if that's at fault .


Have I checked solenoid with correct setting on multimeter? I did it with electricity off.

The resistance check the numbers went up then down to 0 quickly but i pressed hold quickly and got 55.3.

And correct setting for voltage and placing of probes for that?

20250625_234453.jpg
20250625_233822.jpg
20250626_000259.jpg
 

Attachments

  • 20250625_234455.jpg
    20250625_234455.jpg
    202.6 KB · Views: 56
Last edited:
Yes that appears to be a failed solenoid, should be around 4kohm.
 
Have I checked solenoid with correct setting on multimeter? I did it with electricity off.

The resistance check the numbers went up then down to 0 quickly but i pressed hold quickly and got 55.3.

And correct setting for voltage and placing of probes for that?

View attachment 385347View attachment 385348View attachment 385349

Normal coil resistance should be ~ 3.0K to 3.5K.okms, 3000/3500 ohms), Set the resistance scale to 20K and see do youget a steany resistance reading of 3.0 to 3.5 ish, it will not read the correct resistance even on a "good" coil if set to the 200K, I have a old Triton coil in my box and it reads 3.75 on the 20K scale but on the 200K scale jumps around a bit and then reads _1 which is meaningless really.
 
Normal coil resistance should be ~ 3.0K to 3.5K.okms, 3000/3500 ohms), Set the resistance scale to 20K and see do youget a steany resistance reading of 3.0 to 3.5 ish, it will not read the correct resistance even on a "good" coil if set to the 200K, I have a old Triton coil in my box and it reads 3.75 on the 20K scale but on the 200K scale jumps around a bit and then reads _1 which is meaningless really.

Do you think he will understand any of that?

:LOL: :LOL: :LOL: :LOL: :LOL: :LOL: :LOL: