Hello good people - one for the knowledgable sparks here....
I have bought a house which has a small warehouse unit on the land, which has its own 100Amp 3 Phase supply. I have concerns over the installation so I've asked 3 electricians now to come and take a look, and I am getting conflicting advice.
My initial concnern was that I could not see an earth connection on the distribution board in the warehouse unit, and I could see an earth cable coming off the grid supply in the meter cabinet, but it is NOT connected to anything, and by the looks of it, never was.
The service comes into a meter cabinet in a field, (see picture). There is an isolator switch (not fused) which connects to a 4-core armoured cable which runs about 80m to the warehouse where it is terminated to metal trunking and connected to the distribution board. There is no earthing arrangement on the board, no rods etc... Some of the circuits on the board are protected with RCBOs but there is no main incoming RCD.
Electrician #1 Says I have a TT supply, the grid do not give me an earth, and I should have an earth rod at the warehouse. However the building is earthed through the structure, which is fine. He tested earth fault impedence at 16 Ohms and said this should be under 200, and no work needed doing.
Electrican #2 Says I have a PME supply which has not been correctly installed. He says the unconnected earth on the grid supply should be connected to the armoured cable strands, and at the warehouse there should be a similar arrangement to take the earth into the distribution board. Additionally, he says the isolator switch in the meter cabinet should be changed for a fused device at 63 amps to protect the armoured cable.
Electrican #3 Did not comment on the type of earthing, but advised I should have an earth rod installed, and upgrade the breakers in the board to RCD devices.
I have logged an enquiry with Western Power / National Grid to ask what sort of supply I have too.
My gut feeling is that Electrician #2 is right, he seemed a lot more experienced but I would be grateful for other opinions.
Thank you
I have bought a house which has a small warehouse unit on the land, which has its own 100Amp 3 Phase supply. I have concerns over the installation so I've asked 3 electricians now to come and take a look, and I am getting conflicting advice.
My initial concnern was that I could not see an earth connection on the distribution board in the warehouse unit, and I could see an earth cable coming off the grid supply in the meter cabinet, but it is NOT connected to anything, and by the looks of it, never was.
The service comes into a meter cabinet in a field, (see picture). There is an isolator switch (not fused) which connects to a 4-core armoured cable which runs about 80m to the warehouse where it is terminated to metal trunking and connected to the distribution board. There is no earthing arrangement on the board, no rods etc... Some of the circuits on the board are protected with RCBOs but there is no main incoming RCD.
Electrician #1 Says I have a TT supply, the grid do not give me an earth, and I should have an earth rod at the warehouse. However the building is earthed through the structure, which is fine. He tested earth fault impedence at 16 Ohms and said this should be under 200, and no work needed doing.
Electrican #2 Says I have a PME supply which has not been correctly installed. He says the unconnected earth on the grid supply should be connected to the armoured cable strands, and at the warehouse there should be a similar arrangement to take the earth into the distribution board. Additionally, he says the isolator switch in the meter cabinet should be changed for a fused device at 63 amps to protect the armoured cable.
Electrican #3 Did not comment on the type of earthing, but advised I should have an earth rod installed, and upgrade the breakers in the board to RCD devices.
I have logged an enquiry with Western Power / National Grid to ask what sort of supply I have too.
My gut feeling is that Electrician #2 is right, he seemed a lot more experienced but I would be grateful for other opinions.
Thank you