The efficiency figures you find quoted by manufacturers and in the Sedbuk database are annual averages, calculated according to a set formula. It takes into account the fact that the boiler will not always be condensing.You beat me to it! I was going to ask why our condensing boiler (and others) have the option of a wide range of CH temperature settings when only max is recommended?
I don't thinks an explanation would help too much - it might send some to sleep!You had better explain Gross and Net heat inputs; the concept of 106% efficiency will may not be grasped by OP and others.
The efficiency figures you find quoted by manufacturers and in the Sedbuk database are annual averages, calculated according to a set formula. It takes into account the fact that the boiler will not always be condensing.You beat me to it! I was going to ask why our condensing boiler (and others) have the option of a wide range of CH temperature settings when only max is recommended?
To give just one example, the Remeha 18V quotes the following spec:
Input: 18kW
Output at 80/60: 17.6kW
Efficiency at 80/60: 98% (not condensing)
Output at 50/30: 19kW
Efficiency at 50/30: 106% (condensing)
Sedbuk Efficiency: 90.5%
For a boiler to condense, the return temperature has to be below 55°C. (approx).