    Out of interest who gets the final blame if something goes wrong, the installer or manufacturer.

    I am about to fit a 14.1kw ceramic hob range cooker. I enquired of the manufacturer what breaker and cable connections they require. I stated that according to my calcs I could use 6mm with a 32A breaker (allowing for diversity) The reply came back use 6mm with a 40A breaker.

    Although I can see this being ok if the wiring is clipped direct, any other method and the cable rating falls below the breaker rating.

    So if anything did go wrong with the 40A 6MM config. who would get the blame legally. I know I will in reality :)
     
  2. Lectrician

    Lectrician

    Joined:
    18 Jul 2004
    Messages:
    8,506
    Thanks Received:
    405
    Location:
    Devon
    Country:
    United Kingdom
    The manufacturer cannot tell you what cable to use - They can tell you what the maximum current demand is (with diversity perhaps), and you then install a supply accordingly.

    They may say 6mm², but perhaps meaning the final tail? (which is usually H07 type)
     
  3. Sponsored Links
  4. PrenticeBoyofDerry

    PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    21,627
    Thanks Received:
    2,382
    Location:
    Londonderry
    Country:
    United Kingdom
    Follow the manufacturers instruction supplied with the appliance and the IEE wiring regulations. Then the responsibility is the manufacturers, if the appliance does not function as it should.
    Simples!
     
  5. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,663
    Thanks Received:
    3,191
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    As you say,they cannot (or should not!) say anything about what cable to use, not the least because that will depend on installation method. However, what they usually do specify is the rating of the protective device - leaving the user to then ensure that the cable, with its installation method, is adequate to be protected by the OPD in question. Whilst some do say things like "MCB of at least 32A", it quite common to see "...must be protected by a 32A MCB" (regardless of cable size), perhaps implying that they are relying on the circuit's MCB to protect the actual appliance (rather than installiong their own internal protection). In that situation, they might try claiming that it was the user's fault if overcurrent damage occurred to an appliance which was protected by an OPD higher in rating than they said "must" be used.

    Nor is this restricted to large appliances. MIs for small extractor fans often/usually say that they 'must' be protected by a 3A fuse, regardless of cable size.

    Kind Regards, John
     
  6. Sponsored Links
  7. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    All the above is true - the manufacturer can tell you that the hob requires a 40A supply, but not whether you need 6mm², 10mm² or even 16mm² cable.
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page