Hi knowledgeable folks,
Background info. We have a very normal system consisting of a Worcester 24i Junior (non condensing) and DHW/CH. It has a filling loop.
The Issue: Over time the system pressure drops and the boiler cuts out. This typically takes a month to 3 months depending on time of year; however, the other week when it was very cold it happened twice in short succession. When filling via filling loop, the pressure climbs when the taps is open, but above about 1.3 to 1.5 bar it always drops down immediately when I close the filling loop isolation valve. It usually settles around 1.2 Bar. We notice some leakage out the overflow/prv outlet when this happens. However, we NEVER observe any discharge when the boiler is running and pressure can go up to 2.5 Bar.
Recently I noticed that when hot, the system was getting up to 2.7/8 Bar which is too high according tor the manual, so I thought maybe the expansion vessel was under pressure.
What we've checked / tried: Followed the instructions for checking the expansion pressure, and increased from 0.7 Bar to 0.9 (I think, forgot to write it down). This was with the boiler off, and pressure vented via radiator.
Since then, we've also had a boiler inspection / maintenance carried out and they've recommended checking (again) the expansion vessel pre-charge pressure, and replacing the PRV and this is where I'm confused....
Conundrum:
If it were the PRV, why does it only open when the cold water filling loop is open? When it's hot and running at 2.3-2.5bar, the PRV is closed and no water comes out the overflow. Is that system separate? Is there a non-return valve between the hot side and filling side? If so, is that not the issue?
I'm loath to spend £100+ to replace a PRV without it being fairly certain it's going to fix the issue.
Background info. We have a very normal system consisting of a Worcester 24i Junior (non condensing) and DHW/CH. It has a filling loop.
The Issue: Over time the system pressure drops and the boiler cuts out. This typically takes a month to 3 months depending on time of year; however, the other week when it was very cold it happened twice in short succession. When filling via filling loop, the pressure climbs when the taps is open, but above about 1.3 to 1.5 bar it always drops down immediately when I close the filling loop isolation valve. It usually settles around 1.2 Bar. We notice some leakage out the overflow/prv outlet when this happens. However, we NEVER observe any discharge when the boiler is running and pressure can go up to 2.5 Bar.
Recently I noticed that when hot, the system was getting up to 2.7/8 Bar which is too high according tor the manual, so I thought maybe the expansion vessel was under pressure.
What we've checked / tried: Followed the instructions for checking the expansion pressure, and increased from 0.7 Bar to 0.9 (I think, forgot to write it down). This was with the boiler off, and pressure vented via radiator.
Since then, we've also had a boiler inspection / maintenance carried out and they've recommended checking (again) the expansion vessel pre-charge pressure, and replacing the PRV and this is where I'm confused....
Conundrum:
If it were the PRV, why does it only open when the cold water filling loop is open? When it's hot and running at 2.3-2.5bar, the PRV is closed and no water comes out the overflow. Is that system separate? Is there a non-return valve between the hot side and filling side? If so, is that not the issue?
I'm loath to spend £100+ to replace a PRV without it being fairly certain it's going to fix the issue.