Hi all and thanks in advance for your help. I am sending power to my shed about 25 mtrs from the house.
What cable size did your voltage drop calculations produce?
What voltage drop will you get with that?
What will it contribute to the fault-loop impedance of the final circuits in the shed?
to a new consumer unit in the shed.
Why do you think a CU is necessary there?
(i have not enough cable to run double)
Why do you think that your design should be based on what cable you happen to have to hand?
The new consumer unit will have all sockets on a 25 amp MCB ring main
What made you decide that a ring was a better idea than a radial?
and three strip lights on a 6amp MCB also ring main
Why on earth are you planning a ring for a lighting circuit?
My concern is, will it be safe to run a hobby mig welder?
On the basis of the evidence so far, I'd say that there's a significant chance that it won't be.
On the subject of safety, what tests will you be carrying out on the installation in the shed - what sequence will you do them in and at what point will you energise the installation? For each test do you know what is being measured, why it is important, how you would carry out the test, and with what equipment, and what sort of results you would expect to get if everything was OK?
It is the single 27 amp 2.5 twin and earth that concerns me. This is going undergroung and being sheathed.
You can't use that. But even if you could - why do you describe it as "27 amp" cable? What's the installation method for cable installed that way, and what would be the current carrying capacity of 2.5mm² T/E with that method?
Please note that none of the questions I have asked are rhetorical - they are all real and genuine questions, and if you are competent to do this work you will be able to answer them.
Also, are you aware that what you are proposing is notifiable, so you need to apply for Building Regulations approval in advance?
And are you aware that you need permission from your
DNO to use a welder?