Wiring in some Halogens

Joined
4 Jan 2006
Messages
13
Reaction score
0
Location
Berkshire
Country
United Kingdom
Hi guys,

I know this may have been posted before, but haven't found anything answering my exact questions.

Here below is my celling rose on the landing. It is operated by 2 separate switches, one in the hall and the other on the landing.



I plan to put a 6x50W spot bar in and just need to check something as I haven't done this for a while and not with one that has 2 switches coming from it.

The switch live I know goes straight into the live block on the new fixture.

-- Can I terminate the 2 pairs of live red wires together, for example into a wago block? If not, what do I do?

-- I seem to have 3 black wires. Is one or more of these a live return to the switch? Where would that go to?

Thanks, Phil
 
Joined
27 Aug 2003
Messages
69,757
Reaction score
2,884
Location
London
Country
United Kingdom
Hi guys,

I know this may have been posted before, but haven't found anything answering my exact questions.
http://www.diynot.com/wiki/electrics:rose


I plan to put a 6x50W spot bar in and just need to check something as I haven't done this for a while and not with one that has 2 switches coming from it.
The fact that there are 2 switches is irrelevant - only one is connected to the rose.


-- Can I terminate the 2 pairs of live red wires together, for example into a wago block? If not, what do I do?
Or choc-block, or use a 4-terminal lighting JB....


-- I seem to have 3 black wires. Is one or more of these a live return to the switch? Where would that go to?
No - they are all neutrals. They all go to the neutral terminal of your light, or the neutral terminal in your lighting JB.

Don't allow the red sleeving to drop off the black which is not a neutral...
 
Sponsored Links
Joined
4 Jan 2004
Messages
4,020
Reaction score
597
Country
United Kingdom
-- Can I terminate the 2 pairs of live red wires together, for example into a wago block? If not, what do I do?
Thanks, Phil
Follow the ceiling rose instructions BAS referred to.
The only issue with what ever you use to connect the cables make sure, if they are pushed up into the loft you remove the insulation that appears to be covering the current ceiling rose.
 
Joined
28 Jul 2006
Messages
20,912
Reaction score
2,195
Location
Oxfordshire
Country
United Kingdom
Whatever you use to terminate the conductors, the connection blocks must be in a proper enclosure (eg a "ChocBoxTM, or similar contraption) that provides strain relief for the cables.
 
Sponsored Links