Dear all
The pressure starts dropping rapidly in our Worcester 24CDI RSF boiler two weeks after I re charged the expansion vessel to 0.7 bar.
The following tests have been carried out
• Filling the system, leaving it over night no demand for DWH or CH the pressure does not drop at all.
• Checked all the pipes work under the floor broad and all the radiators connection and valves, I noticed no leak at all, and I do not there a leak in the firs floor pipe work, otherwise we would have noticed a big patch in the ceiling considering the rate it is dropping.
• Switch on the CH only for couple of hours then switch it off let the system cool down, I noticed there is not pressure drop at all.
• Checked inside the boiler including the Gas to Water Heat Exchange and found no trace of leak at all
• The drop of pressure happened when there is a demand for DHW, i.e when we take a shower for 10 minutes the pressure drops two digits i.e from 1 bar to 0.8 bar.
• This leaves me to conclude that the water to water heat exchanger is faulty. I believe some of the CH loop water is sucked in through one of the water to water heat exchanger inner pipes or walls and joins the DHW out of the system.
Is this possible or am I stretching my imagination, any help reply would be highly appreciated as this is driving me made.
The pressure starts dropping rapidly in our Worcester 24CDI RSF boiler two weeks after I re charged the expansion vessel to 0.7 bar.
The following tests have been carried out
• Filling the system, leaving it over night no demand for DWH or CH the pressure does not drop at all.
• Checked all the pipes work under the floor broad and all the radiators connection and valves, I noticed no leak at all, and I do not there a leak in the firs floor pipe work, otherwise we would have noticed a big patch in the ceiling considering the rate it is dropping.
• Switch on the CH only for couple of hours then switch it off let the system cool down, I noticed there is not pressure drop at all.
• Checked inside the boiler including the Gas to Water Heat Exchange and found no trace of leak at all
• The drop of pressure happened when there is a demand for DHW, i.e when we take a shower for 10 minutes the pressure drops two digits i.e from 1 bar to 0.8 bar.
• This leaves me to conclude that the water to water heat exchanger is faulty. I believe some of the CH loop water is sucked in through one of the water to water heat exchanger inner pipes or walls and joins the DHW out of the system.
Is this possible or am I stretching my imagination, any help reply would be highly appreciated as this is driving me made.