Hi all,

I moved into a house recently and noticed that the heaters and not working very efficiently. I noticed that the pressure gauge is below 1 and by searching online I saw i need to repressurize the system. I am looking for the little flexi pipe to allow some water in but after searching for hours I cannot find it and would be greatful for some advice where it could
 
Joined
1 Dec 2021
Messages
1,250
Reaction score
158
Country
Ireland
Find your water inlet (mains in or to the head tank) and trace
 
Sponsored Links
Joined
9 Sep 2005
Messages
12,716
Reaction score
3,440
Location
Sussex
Country
United Kingdom
Pressurise to 1 Bar max and then watch the gauge as the radiators heat up, turn the heating off if it creeps pass 2 bar, the chances are the expansion vessel is flat and needs sorting.
 
Joined
22 Jan 2007
Messages
6,790
Reaction score
1,213
Country
United Kingdom
I am looking for the little flexi pipe to allow some water in but after searching for hours I cannot find

One end of it is shown below, can you check above the boiler or see anything at all from below?