Hi guys
Just looking for a little assistance on this as its puzzled me.
Got called out to a 40 CDI today that wasnt firing. Upon enquiring, customer advised that many parts had previously been replaced... namely; Fan, gas valve, primary heat exchanger... All by worcester bosch engineers. The boiler had been working fine for about 6 months but now doesnt seem to fire.
Strangely though i found that the boiler ONLY fires and remains lit when i block the air intake. Assumption here is that the air gas mixture is all wrong so removed fan to check diaghragm in airway and all seems fine. Diaghragm is intact and in good nick checked all flue seals etc but cant see why the boiler will only fire up when i put my hand accross the air intake.
My initial thoughts were to complete a flue analysis but im not sure how helpful thats going to be if i have to interfere with the air intake in order to do keep the boiler fired up... I can say however that the CO levels were through the roof though. Flue analyser went nuts.
Any thoughts
Many thanks in advance
Ps gas inlet pressure checked and all fine
Just looking for a little assistance on this as its puzzled me.
Got called out to a 40 CDI today that wasnt firing. Upon enquiring, customer advised that many parts had previously been replaced... namely; Fan, gas valve, primary heat exchanger... All by worcester bosch engineers. The boiler had been working fine for about 6 months but now doesnt seem to fire.
Strangely though i found that the boiler ONLY fires and remains lit when i block the air intake. Assumption here is that the air gas mixture is all wrong so removed fan to check diaghragm in airway and all seems fine. Diaghragm is intact and in good nick checked all flue seals etc but cant see why the boiler will only fire up when i put my hand accross the air intake.
My initial thoughts were to complete a flue analysis but im not sure how helpful thats going to be if i have to interfere with the air intake in order to do keep the boiler fired up... I can say however that the CO levels were through the roof though. Flue analyser went nuts.
Any thoughts
Many thanks in advance
Ps gas inlet pressure checked and all fine