worcester greenstar boiler fault

Joined
22 Dec 2011
Messages
2
Reaction score
0
Location
Humberside
Country
United Kingdom
Help needed for Worcester Bosch Greenstar R1. On fire up makes whooshing noise like filling with water. Green burner light is intermittent until eventually goes out altogether when boiler goes to lockout. Have checked whether air in boiler and seems ok. When system runs just with pump going no signs of air in system.

Strangely left pump running all night and boiler fired up perfectly this morning for about 10 minutes and then went into lock out.

Supect it is one of the sensors any thoughts. Thanks Colin
 
Sponsored Links
Have a look at the model again, I don't think R1 exists! Could it be Ri? Is it a combi? And does it have a display with a lockout code on it or does it just have flashing lights? If so, what's the code or flashing light sequence?
 
Sponsored Links
Thanks to Agile.

Answer 100% correct. Had changed piece of condensate drain pipe before completing cupboard work around boiler. Suspected box may have caused boiler to overheat. Surprisingly found pipe work was blocked with debris.As drain pipe only used old pipe from workshop. Briliant answer from Agile..saved a fortune. Merry Xmas and thanks.
 