Working Near Mains Equipment, This Is What Can Happen!

Joined
3 Jan 2011
Messages
2,497
Reaction score
314
Location
Cumberland
Country
United Kingdom
CUST STATES THEY SUSTAINED FLASH BURNS ON SATURDAY UNSURE WHAT IS WRONG WITH MAINS COMING INTO HOUSE CUST IS STAYING AWAY CUST WAS INJURED SEVERELEY AND HOSPITALISED SINCE SATURDAY - cons has been renovating prop & has chisled through cement around incoming u/gs cable & has penetrated ducting & cable - reqs new piece of service putting in tonight (AS)

This is a single phase service probably with a 315A fuse at the substation which did not operate

Rare but it does happen!!
 
Sponsored Links
CUST STATES THEY SUSTAINED FLASH BURNS ON SATURDAY UNSURE WHAT IS WRONG WITH MAINS COMING INTO HOUSE CUST IS STAYING AWAY CUST WAS INJURED SEVERELEY AND HOSPITALISED SINCE SATURDAY - cons has been renovating prop & has chisled through cement around incoming u/gs cable & has penetrated ducting & cable - reqs new piece of service putting in tonight (AS)
This is a single phase service probably with a 315A fuse at the substation which did not operate. Rare but it does happen!!
If it can happen, it will happen (sooner or later)!

Does your employer offer English classes to it's employees? :)

Kind Regards, John
 
This is a single phase service probably with a 315A fuse at the substation which did not operate.
As a matter of interest .... do the regulations under which you operate have a requirement analogous to that of BS7671, such that the loop impedance at the furthest supplied service has to be low enough for the OPD protecting it to operate (in response to a L-E or L-N fault of negligible impedance) within a specified time?

Kind Regards, John
 
Sponsored Links
As a matter of interest .... do the regulations under which you operate have a requirement analogous to that of BS7671, such that the loop impedance at the furthest supplied service has to be low enough for the OPD protecting it to operate (in response to a L-E or L-N fault of negligible impedance) within a specified time?

Simple answer, no!
This one was actually only about 80m route length from a substation.

At the end of the day with this type of incident there are no absolutes, the fuse may or may not operate, the customer may or may not get injured, the cable may or may not burn open circuit, the cable may or may not end up carrying enough current to burn back or damage the insulation etc.
 
Simple answer, no! This one was actually only about 80m route length from a substation.
At the end of the day with this type of incident there are no absolutes, the fuse may or may not operate, the customer may or may not get injured, the cable may or may not burn open circuit, the cable may or may not end up carrying enough current to burn back or damage the insulation etc.
That's obviously all true, but analogous things are equally true within an installation, in relation to which BS7671 does impose requirements in terms of automatic disconnection in response to negligible impedance faults.

Are you saying/implying that you are subject to no regulatory requirements relating to the operation of protective devices in response to faults?

Kind Regards, John
 
Read ESQCR

All it says

Electrical protection

6. A generator or distributor shall be responsible for the application of such protective devices to his network as will, so far as is reasonably practicable, prevent any current, including any leakage to earth, from flowing in any part of his network for such a period that that part of his network can no longer carry that current without danger.

and

Precautions against supply failure

23. (1) A distributor shall ensure that his network shall be—

(a)so arranged; and

(b)so provided, where necessary, with fuses or automatic switching devices, appropriately located and set, as to restrict, so far as is reasonably practicable, the number of consumers affected by any fault in his network.

But note the words
so far as is reasonably practicable

To design a network to operate as an installation should be is not reasonably practicable, so within the uncertainty of what can occur we have what we have.

As discussed many times there is not a BS7671 equivalent for the DNOs, we are fairly free to set our own and differing parameters to operate our networks as long as we comply with the deliberately vague requirements of legislation. (just as legislation, Part P, does not require strict observance of BS7671, just that safety is ensured. BS7671 is one way of doing this)
 
Read ESQCR. All it says
Electrical protection
6. A generator or distributor shall be responsible for the application of such protective devices to his network as will, so far as is reasonably practicable, prevent any current, including any leakage to earth, from flowing in any part of his network for such a period that that part of his network can no longer carry that current without danger.
OK - so, as you say, pretty vague, and with a let-out if to achieve even that would not be (in whoever's mind!) "reasonably practicable".
...and
Precautions against supply failure
23. (1) A distributor shall ensure that his network shall be—
(a)so arranged; and
(b)so provided, where necessary, with fuses or automatic switching devices, appropriately located and set, as to restrict, so far as is reasonably practicable, the number of consumers affected by any fault in his network.
Fair enough - but that one has obviously got nothing directly to do with 'electrical safety'.
... As discussed many times there is not a BS7671 equivalent for the DNOs, we are fairly free to set our own and differing parameters to operate our networks as long as we comply with the deliberately vague requirements of legislation. (just as legislation, Part P, does not require strict observance of BS7671, just that safety is ensured. BS7671 is one way of doing this)
That's all true but, in practice, in terms of installations, I think one would probably be very hard pressed to successfully argue that one had complied with the legislation (part P) if one had failed to satisfy disconnection times explicitly specified in BS7671, and probably would be 'laughed out of court' if one's explanation for this failure was that it was considered not to be "reasonably practicable" to design/install cable of an adequate CSA to satisfy the BS7671 requirement!

I suspect one thing you may be overlooking is that it is (presumably) generally DNOs, not individual employees of DNOs, who decide on how to interpret and implement ESQCR (and with whom the buck stops as regards deciding what is "reasonably practicable"), which is probably reasonable. However, in terms of installations, most work is undertaken by independent electricians or small companies - and I really don't think it would be reasonable, sensible or workable to have individual electricians (and 'electricians')!, or thousands of small companies, making their own decisions as to, say, what 'disconnection times' were required in order to satisfy Part P. Hence the need for the more specific guidance of omething like BS7671.

Kind Regards, John
 
it is (presumably) generally DNOs, not individual employees of DNOs,

Everyone of our Codes of Practice that shows how we should comply is signed by an individual responsible officer. If it goes wrong that officer can be (and has been) arrested and cautioned!

However, in terms of installations, most work is undertaken by independent electricians or small companies - and I really don't think it would be reasonable, sensible or workable to have individual electricians (and 'electricians')!, or thousands of small companies, making their own decisions as to, say, what 'disconnection times' were required in order to satisfy Part P. Hence the need for the more specific guidance of omething like BS7671

Quite true but that doesn't, in some ways excuse the depth of detail in that document.

but that one has obviously got nothing directly to do with 'electrical safety'.

True, a bit like the apparently near absolute requirement for split boards in BS7671 isn't it!
 
it is (presumably) generally DNOs, not individual employees of DNOs,
Everyone of our Codes of Practice that shows how we should comply is signed by an individual responsible officer. If it goes wrong that officer can be (and has been) arrested and cautioned!
Yes, obviously - but although an individual may be responsible (and accountable), the Code of Practice is a corporate one applying to all employees of the DNO, and there's only a tiny handful of DNOs. That's very different from tens of thousands of individual electricians creating their own personal 'Code of Practice' based on their understanding (if they have any!) of what is required to satisfy Part P!
Quite true but that doesn't, in some ways excuse the depth of detail in that document.
I'm not so sure. Given the very wide spectrum of knowledge/ competence/ experience of electricians (and 'electricians'), which is many cases is probably negligible in comparison with the 'corporate knowledge' of a DNO, I think that some of them probably need as much detail as can be provided!
True, a bit like the apparently near absolute requirement for split boards in BS7671 isn't it!
It is, and is an example of (probably desirable) vagueness. The "apparently near absolute requirement" exists only for those who chose to interpret "avoid danger and minimize inconvenience" and/or "taking into account the hazards that may arise from failure of a single circuit" in that way!

Kind Regards, John
 
I'd imagine the Pfc to be fairly high there, into the 1000s of amps. Ouch!
 
I'd imagine the Pfc to be fairly high there,

Yep from memory of the cable records about 10kA


If that were the case, would not one have expected a 315A fuse to have operated fairly smartish

Nope as often the explosion blows the fault clear to an open circuit, you would be surprised the amount of damage that can be seen and still found to be live. This applies at higher voltages as we've had cases of badly damaged 6.6kV cables still live
 